Elekton. VSDs

Post by BoretsMV »

A decrease in flash isolation is observed. In fact, the measurement was 10 mOhm (confirmation by flash from the ground unit TMSN). In principle, everything is clear. It’s just that before I wrote this, I didn’t have any flash information on hand.
hde08a4c.rar
Original reply
Снижение изоляции по флэш наблюдается. По факту замер 10 мОм (подтверждение флэш с наземного блока тмсн). В принципе все понятно. Просто до того как написать не было флэш информации на руках.
You do not have the required permissions to view the files attached to this post.
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Elekton. VSDs

Post by ALEngineer »

According to TMS, the insulation is around 10 MOhm, too, and the insulation is constantly reduced, but for some reason this information did not reach the controller, perhaps TMS is not connected correctly. Check the operation of the TMSN protection using insulation, a shunt or a piece of wire. Stopping at R-0 is most likely a glitch.
Judging by the log, there are no external prerequisites for IGBT accidents, some kind of hardware failure is occurring, this is clearly visible from the Id graph in the emergency log, in all three cases.
I recommend calling a service representative Elekton to sort out the situation.
Original reply
По ТМС изоляция в районе 10МОм тоже, при чем постоянно изоляция снижена, а до контроллера по какой то причине эта информация не дошла, возможно ТМС обвязана не правильно. Проверьте срабатывание защиты ТМСН по изоляции, шунтом или куском провода. Остановка по R-0 это скорее всего глюк.
Судя по журналу, внешних предпосылок для аварий по IGBT нет, происходит какой то аппаратный сбой, это четко видно по графику Id в аварийном журнале, во всех трех случаях.
Рекомендую вызвать представителя сервисной службы Электон, что бы разобраться в ситуации.
BoretsMV
Posts: 9
Joined: Wed May 21, 2014 11:56 pm

Elekton. VSDs

Post by BoretsMV »

Thank you, we will work in both directions.
Original reply
Спасибо, отработаем в обоих направлениях.
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Elekton. VSDs

Post by ALEngineer »

User Maxim shared software for VSD Elekton

https://yadi.sk/d/l7WRCrSTrkCs2
Original reply
Пользователь Максим поделился ПО для СУ Электон

https://yadi.sk/d/l7WRCrSTrkCs2
RKurmanov
User avatar
Posts: 4
Joined: Thu Oct 06, 2016 7:24 am

Elekton. VSDs

Post by RKurmanov »

VFD Elekton 05 2009 at the input to the station 405 volts at the output 425 volts base frequency 51 hertz voltage at 4 points 380 how can this be?
Original reply
станция управления электон 05 2009г на входе в станцию 405вольт на выходе 425вольт базовая частота 51герц напряжение в 4точке 380 как так может быть?
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Elekton. VSDs

Post by ALEngineer »

Did you measure the voltage or does VFD show the calculated voltage? If measured, then with what? Chinese cheap devices will not be able to measure the voltage at the output of the frequency VFD and will show the “weather”. We need a device with RMS technology. Measurements should be made under load, otherwise the VFD will fail.
Original reply
Напряжение замеряли или СУ показывает расчетное? Если замеряли, то чем? Китайские дешевые приборы не смогут в принципе измерить напряжение на выходе частотной СУ и покажут "погоду". Нужен прибор с технологией RMS. Измерять следует под нагрузкой, иначе выйдет из строя СУ.
RKurmanov
User avatar
Posts: 4
Joined: Thu Oct 06, 2016 7:24 am

Elekton. VSDs

Post by RKurmanov »

measured with a Fluke 80 SeriesV multimeter, the load was a 160 kVA transformer through a Elekton 400a filter
Original reply
замеряли мультиметром FLUKE 80 SeriesV нагрузкой был трансформатор 160 кVA через фильтр электон 400а
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Elekton. VSDs

Post by ALEngineer »

VFD Elekton do not work as boost converters. Most likely there was a measurement error. If I'm not mistaken, then the 80th Fluke does not have the RMS functionality on board; if this is so, then it will not be able to take measurements on frequency converters in principle, especially with a frequency other than 50Hz. Fluke 113 or 117 should have this technology. When attaching a photo of a device with RMS technology, TRUE RMS must be clearly written on the device. Such devices are capable of calculating the current values ​​of current and voltage with a signal shape other than a sinusoid (and VFD do not produce a sinusoid at the output, Elekton is no exception, for this purpose they install output filters in order to reduce the heating of the equipment at the output). Also, these devices operate correctly at frequencies other than 50Hz.
Fluke-117-Review.png
Original reply
СУ Электон не работают как повышающие преобразователи. Скорее всего ошибка при измерении. Если я не ошибаюсь, то 80-тый Флюк не имеет функционала RMS на борту, если это так, то он и не сможет произвести замер на частотных преобразователях в принципе, тем более с частотой отличной от 50Гц. Флюк 113 или 117 должен иметь данную технологию. В приложении фото прибора с технологией RMS, на приборе должно быть явно прописано TRUE RMS. Такие приборы способны посчитать текущие значения тока и напряжения при форме сигнала отличного от синусоиды (а СУ ЧР выдают на выходе НЕ синусоиду, Электон не исключение, для того и ставят выходные фильтра, с целью уменьшения нагрева оборудования на выходе). Так же данные приборы корректно работают на частотах отличных от 50Гц.
You do not have the required permissions to view the files attached to this post.
RKurmanov
User avatar
Posts: 4
Joined: Thu Oct 06, 2016 7:24 am

Elekton. VSDs

Post by RKurmanov »

thanks for the information! everything is clear now!
Original reply
спасибо за информацию!теперь все ясно!
Добрый Кот
User avatar
Posts: 31
Joined: Wed Oct 12, 2016 11:50 am

Elekton. VSDs

Post by Добрый Кот »

Has anyone encountered this:
Elekton-05 400, when starting at idle, i.e. without load, shows ~20A at the output for each phase, measured with clamps inside VSD - this is really true.
If with a load, with a stand, then the first few stages are greatly overestimated (at first by about 20, then with each stage less and less), it levels out at approximately a load of 40 kW.
The electrical engineers said that this happens. But “this happens” cannot be applied to test results.
Original reply
Кто-нибудь сталкивался с таким:
Электон-05 400, при запуске на холостом ходу, т.е. без нагрузки, показывает ~20А на выходе по каждой из фаз, замеряли клещами внутри СУ - это реально так.
Если с нагрузкой, со стендом, то первые несколько ступеней сильно завышены (сначала примерно на 20, потом с каждой ступенью всё меньше), выравнивается примерно на нагрузке 40кВт.
Электонщики сказали, мол бывает такое. Но "бывает такое" к результатам теста не приложишь.