According to TMS, the insulation is around 10 MOhm, too, and the insulation is constantly reduced, but for some reason this information did not reach the controller, perhaps TMS is not connected correctly. Check the operation of the TMSN protection using insulation, a shunt or a piece of wire. Stopping at R-0 is most likely a glitch.
Judging by the log, there are no external prerequisites for IGBT accidents, some kind of hardware failure is occurring, this is clearly visible from the Id graph in the emergency log, in all three cases.
I recommend calling a service representative Elekton to sort out the situation.
Original reply
По ТМС изоляция в районе 10МОм тоже, при чем постоянно изоляция снижена, а до контроллера по какой то причине эта информация не дошла, возможно ТМС обвязана не правильно. Проверьте срабатывание защиты ТМСН по изоляции, шунтом или куском провода. Остановка по R-0 это скорее всего глюк.
Судя по журналу, внешних предпосылок для аварий по IGBT нет, происходит какой то аппаратный сбой, это четко видно по графику Id в аварийном журнале, во всех трех случаях.
Рекомендую вызвать представителя сервисной службы Электон, что бы разобраться в ситуации.