Has anyone replaced the controller on an Elekton-05 VSD without stopping the well?

Today I hit this: starting ESP from an Elekton 05.09-630A VSD, after about 10 minutes insulation started falling and within 5 minutes it was at zero. I pulled the downhole power cable and meggered it - over 100 MOhm.

I fully disconnected the SIU (surface interface unit, TMS) and started the well without the SIU and without the IMD board. I insulated the Rins lead and the rest of that bundle. After about 15 minutes the same thing happened.

The VSD now runs with the SIU and insulation protection off. After the reading drops to zero, insulation still shows around 90 kOhm. If anyone has seen this, please share how you cleared it.
Original topic
Сегодня столкнулся с такой бедой: при запуске УЭЦН от СУ Электон 05.09-630А приблизительно после 10 минут работы стала снижаться изоляция и за минут 5 упала до нуля.

Откинул и прозвонил погружной кабель, изоляция составила более 100 мОм. Полностью отключил наземный блок ТМС и запустил скважину уже без блока и без платы, провод Riz и все из того пучка заизолировал.

Через примерно минут 15 работы история повторилась. СУ работает с отключенным блоком ТМС и защитой по изоляции, после падения на ноль показания по сопротивлению изоляции в районе 90 кОм.

Если у кого нибудь была подобная ситуация, поделитесь информацией по способам устранения. BLK0
BoretsMV
Posts: 10
Joined: Wed May 21, 2014 11:56 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by BoretsMV »

What if you disconnect the "0" wire? If that doesn't help, you can try replacing the controller.
Original reply
А если отключить "0" провод? Если не поможет, то можно попробовать заменить контроллер.
ALEngineer
Site Admin
User avatar
Posts: 703
Joined: Wed Mar 18, 2026 2:51 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by ALEngineer »

Turned it off. The meter is the lower controller, should I change it? Or are there glitches in the top? This is a question purely for myself, because... No one will stop the well.
Original reply
Отключал. Измеритель это нижний контроллер, его менять? Или в верхнем глюки? Уже вопрос чисто для себя, т.к. скважину ни кто остановить не даст.
BoretsMV
Posts: 10
Joined: Wed May 21, 2014 11:56 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by BoretsMV »

Without stopping, you can try the top controller first. Is there a sequence of actions? Or throw it off?
Original reply
Без останова можно попробовать для начала верхний контроллер. Очередность действий есть? Или скинуть?
ALEngineer
Site Admin
User avatar
Posts: 703
Joined: Wed Mar 18, 2026 2:51 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by ALEngineer »

There is no queue. If possible, describe it.
Original reply
Очередности нет. Если можно опишите.
BoretsMV
Posts: 10
Joined: Wed May 21, 2014 11:56 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by BoretsMV »

To replace the controller without stopping the well on Elekton 05, the following measures must be taken:



1.Disable TM

2.Disconnect connector X2 (communication between two controllers);

3.Disconnect connector X1 (external connections)

4.Disconnect connector X3 (power)

5.Change the controller.

6.Connect connector X3 (power)

7. Enter the necessary settings into the controller, calibrate the voltage and currents using clamps and a multimeter.

8.Disconnect connector X3 (power)

9.Connect connector X1 (external connections)

10. Connect connector X3 (power)

11. Connect connector X2 (communication between two controllers);

12. Connect the TM, having previously checked the contacts.



It is imperative to follow the sequence of actions, otherwise a stop will occur due to an “accident VFD” in 15 minutes.
Original reply
Для замены контроллера без остановки скважины на Электоне 05 нужно произвести следующие мероприятия:



1.Отключить ТМ

2.Отключить разъем Х2 (связь между двумя контроллерами);

3.Отключить разъем Х1 (внешние подключения)

4.Отключить разъем Х3 (питание)

5.Поменять контроллер.

6.Подключить разъем Х3 (питание)

7.Внести необходимые уставки в контроллер, откалибровать напряжение и токи по клещам и мультиметру.

8.Отключить разъем Х3 (питание)

9.Подключить разъем Х1 (внешние подключения)

10. Подключить разъем Х3 (питание)

11. Подключить разъем Х2 (связь между двумя контроллерами);

12. Подключить ТМ, предварительно проверив контакты.



Обязательно соблюдать очередность действий, иначе произойдет остановка по «аварии ПЧ» через 15минут.
BoretsMV
Posts: 10
Joined: Wed May 21, 2014 11:56 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by BoretsMV »

Don't forget to remove the flash archive from the old controller
Original reply
Не забудьте снять флэш архив со старого контроллера
ALEngineer
Site Admin
User avatar
Posts: 703
Joined: Wed Mar 18, 2026 2:51 pm

Re: Replacing the controller without stopping the well with Elekton 05

Post by ALEngineer »

Thank you! Let's try!
Original reply
Спасибо! Будем попробовать!