Neutral conductor heating between transformer and VSD

Discuss step-up and step-down transformers, surface cables, and power infrastructure for ESP systems. Share expertise on electrical setups and safety
RAFIS
User avatar
Posts: 5
Joined: Thu Mar 01, 2018 11:47 am

Neutral conductor heating between transformer and VSD

Post by RAFIS »

Good evening colleagues! We hit a problem: the neutral ("0") conductor between the transformer and the VSD is heating up. Has anyone seen this? Grounding circuit is intact.
Original topic
добрый вечер коллеги! Столкнулись с такой проблемой, греется "О" провод между ТП иСУ. Кто нибудь может  сталкивался с такой проблемой. Контур заземления целый.
qwerty
User avatar
Posts: 1
Joined: Wed Mar 06, 2019 6:24 am

Neutral conductor heating between transformer and VSD

Post by qwerty »

Is it a VFD? Most likely the filter. I had it on an Etalon-1600. Only replacing the VSD helped.
Original reply
СУ ЧРП? вероятнее всего фильтр. У меня было с эталоном-1600. Помогло только замена СУ
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

Neutral conductor heating between transformer and VSD

Post by ALEngineer »

So you have a big imbalance. Maybe the rectifier is bad on one phase? If so, input current on one phase will be almost zero. Or a phase-to-ground leak somewhere - then one phase will draw noticeably more.

Either way, with a good ground this should not happen.
Original reply
Получается дисбаланс большой. Возможно выпрямитель по одной фаз не исправен? Если это так, то по входу на одной из фаз практически не будет токов. Либо где то фаза на корпус утечку даёт, тогда наоборот, одна из фаз будет заметно больше потреблять тока. В любом случае, при нормальном заземлении, такого бы не произошло
klocium
User avatar
Posts: 13
Joined: Wed Nov 22, 2017 4:46 am

Neutral conductor heating between transformer and VSD

Post by klocium »

I know a year and a half passed, but the thread is not finished. If the transformer is 6/0.4, maybe the neutral is not grounded in the transformer. We had that. Then the imbalance coming on the 6 kV side stayed on the 0.4 kV side too and only equalized through the VSD with a large leak.

In any case measure leakage currents and check not only line voltage but phase voltage - with a big imbalance one phase can reach line voltage while the other is almost nothing.
Original reply
Понимаю что полтора года прошло, но тема не закончена. Если ТП 6/0,4, то возможно в ТП не заземлена нейтраль. У нас такое было. И соответственно перекос который шёл по 6-ке тоже оставался и в 0,4 и выравнивался только через СУ с большой утечкой. В любом случае нужно мерить токи утечки и проверять не только линейное напряжение , но и фазное, которое при большом перекосе может достигать линейного по одной фазе и не быть совсем на другой.