Hello!
It appeared on Triol AT24-M25-380-UH. I've been fighting it (it pops up randomly) for 3 months now....
After consultation with Triol support, the values of the U/F settings were increased, section [2,*] in VFD.
The values are as follows:
Characteristic No. 1, B
12,60,304, 320, 380.
Characteristic No. 2, B
12, 152,304, 320, 380. Increased U2 from default 60 V to 152 V.
Supply ~U = 408 V. Setting Ud max= 680 V.
If the motor is disconnected from the pump (the coupling half is disassembled), the Ud error is guaranteed to pop up at 26-27 Hz. So if you need to undergo vibration diagnostics, run it at 25 Hz and remove the parameters. If normal, connect the pump, run it at 50 Hz and remove it again.
Original reply
Привет!
У меня появлялась на Триол АТ24-М25-380-UH. Борюсь с ней (выскакивает рандомно) уже месяца 3....
После консультации с саппортом Триолов были увеличены значения настроек U/f , раздел [2,*] в ЧРП.
Значения следующие:
Характеристика №1 ,В
12,60,304, 320, 380.
Характеристика №2 ,В
12, 152,304, 320, 380. Увеличено U2 с 60 В по умолчанию до 152 В.
Питающее ~U = 408 В. Уставка Ud max= 680 В.
Если двигатель отключен от насоса (разобрана полумуфта) - ошибка Ud выскакивает гарантированно на 26-27 Гц. Так что если надо пройти вибродиагностику - запускаем на 25 Гц , снимаем параметры. Если в норме - присоединяем насос, запускаем на 50 Гц и снимаем повторно.