U/F characteristic for PMM on Etalon (Valve Motors) VFD

Etalon ESP variable speed drives: Modbus addressing, alarm handling, parameter setup, and field tips.
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

U/F characteristic for PMM on Etalon (Valve Motors) VFD

Post by ALEngineer »

Characteristics U/F for PMM (Valve Motors) VFD Etalon-AB

Scan / image text translation (original scan kept as attachment below):

Code: Select all

+--+------------------+-------------------------+
|  | VFD ETALON-AB     |                         |
+--+------------------+-------------------------+
|1.| 8 Hz - 12.1%     | base frequency - 120 Hz |
|2.| 30 Hz - 21.3%    | Voltage 380 V           |
|3.| 60 Hz - 42.6%    |                         |
|4.| 90 Hz - 63.5%    |                         |
|5.| 120 Hz - 86.7%   |                         |
+--+------------------+-------------------------+
uf_1.jpg
Original topic
Характеристика U/F для ВЭД (Вентильные Электродвигатели) СУ Станция Управления Эталон-АВ

Перевод текста с картинки (скан сохранён во вложении ниже):

Code: Select all

+--+------------------+-------------------------+
|  | СУ ЭТАЛОН-АВ     |                         |
+--+------------------+-------------------------+
|1.| 8Гц - 12,1%      | базовая частота - 120Гц |
|2.| 30Гц - 21,3%     | Напряжение 380В         |
|3.| 60Гц - 42,6%     |                         |
|4.| 90Гц - 63,5%     |                         |
|5.| 120Гц - 86,7%    |                         |
+--+------------------+-------------------------+
uf_1.jpg
You do not have the required permissions to view the files attached to this post.
chitos3572
Posts: 11
Joined: Wed Sep 10, 2014 11:59 pm

Characteristic U/F for PMM VFD Etalon (Valve Motors)

Post by chitos3572 »

Good afternoon
Not quite correct table.
To set the maximum engine operating frequency, there is a “Limit frequency” setting.
The "Base Frequency" setting sets the slope of the U/F characteristic and must correspond to the rated motor frequency. If this parameter does not correspond to the nominal value for a given motor, then it is necessary to recalculate the rated voltage of the motor in proportion to the set frequency.
Thus, the following is set (for a 100 Hz motor): Base frequency - 100 Hz, Base voltage - 380 V, Limit frequency - 120 Hz, Rated motor voltage - according to the passport.
After setting these parameters, the control algorithm will calculate the U/F characteristic points.
It is advisable to choose a step-up transformer tap such that the 5th point is around 85%
These recommendations are relevant only for a switched-type motor (for VFD PM and switched-type mode VFD AB).
Original reply
Добрый день!
Не совсем верная таблица.
Для задания максимальной частоты работы двигателя существует уставка "Предельная частота" .
Уставка "Базовая частота" задает наклон U/F характеристики и должна соответствовать номинальной частоте двигателя. Если этот параметр не соответствует номинальному для данного двигателя, то необходимо пропорционально к выставленной частоте пересчитать номинальное напряжение двигателя.
Таким образом, выставляется (для 100 Гц двигателя): Базовая частота - 100 Гц, Базовое напряжение - 380 В, Предельная частота - 120 Гц, Номинальное напряжение двигателя - по паспорту.
После выставления этих параметров алгоритм регулирования рассчитает точки U/F характеристики.
Отпайку ТМПН желательно выбрать такую, что бы 5 точка была в районе 85%
Данные рекомендации актуальны только для вентильного двигателя (для СУ ВД и вентильного режима СУ ЧР АВ).