Triol TMN01-09 surface TMS Transfer issues

Technical exchange on permanent downhole monitoring systems. Covers SIU integration, and data reliability from motor base to surface
klocium
User avatar
Posts: 13
Joined: Wed Nov 22, 2017 4:46 am

Triol TMN01-09 surface TMS Transfer issues

Post by klocium »

Hello all!
Any info on this wonder?

We have these SIUs on Transfer protocol. They link with their own simulator (not always), but same protocol with Almaz simulators - no link.

OK, linked in the shop with their simulator - fine. Go to the well, install in the native Triol VSD, connect to native Triol downhole sensor (TMS) - link comes and goes, or drops on start.

Can anyone explain how THIS works and why it was made? Maybe better SIU (surface interface unit, TMS) firmwares exist. Surface units are fresh - July this year. Firmware per board tag 48.468.

Thanks.
Original topic
Здравствуйте всем!
Есть какая либо инфа по данному чуду?
Суть вот в чём: есть данные блоки с протоколом Трансфер, со своим имитатором соединяется (хотя тоже не всегда), но по тому же протоколу с имитаторами Алмаз - соединения нет.
Ладно, соединили в тепличных условиях со своим имитатором, всё в порядке, едем на скважину ставим в родную триоловскую СУ, соединяем со своим родным триоловским ТМСП, соединение то есть, то нет или может отвалиться при запуске.
Может кто-либо пояснить как ЭТО работает? И зачем ОНО создано.
Может есть прошивки на ТМСН более работоспособные, чем эти. ТМСНы свежие июль этого года. Прошивка, судя по шильдику на плате 48.468.
Спасибо.
omega134134
User avatar
Posts: 24
Joined: Thu Dec 06, 2018 8:37 am

Triol TMN01-09 surface TMS Transfer issues

Post by omega134134 »

Tell Charikov to call the Triol plant.
Original reply
Скажи чарикову пусть звонит на завод триоловцам
TMSnick70
User avatar
Posts: 25
Joined: Wed Jan 02, 2019 11:41 am

Triol TMN01-09 surface TMS Transfer issues

Post by TMSnick70 »

I suspect developer unfinished work. Saw several surface units - no auto level correction, no proper edge correction. No downhole sensor (TMS) has output pre-distortion. Manchester is decoded in software (who knows how) by the MCU via ADC whose input is mangled beyond recognition by cable, chokes, and filter caps. Each maker built downhole for their own surface unit. That the protocol is "common" apparently did not land.
Original reply
Предполагаю что подобные проблемы связаны с недоработками разработчиков. Видел несколько наземников. На них нет ни автокоррекции уровня, ни нормальной коррекции фронтов сигнала. Ни в одном погружном блоке нет предискажений выходного сигнала. Манчестер декодируется программно(т.е. хз как) микроконтроллером через АЦП, на входе которого сигнал перекосоёбен характеристикой кабеля, дросселями и конденсаторами фильтров до неузнаваемости. Каждый производитель городил свой погружной блок под свой наземник. А то что протокол общий, то видимо до них это не дошло.
Yurii Z.
User avatar
Posts: 4
Joined: Fri Jul 27, 2018 3:54 am

Triol TMN01-09 surface TMS Transfer issues

Post by Yurii Z. »

Anything resolved? How do Triol TM-01-09 units behave - worth buying, or avoid?
Original reply
что-то решилось? Есть информация как работают ТМ-01-09 ТРИОЛ, стоит покупать? Или обойти стороной?
klocium
User avatar
Posts: 13
Joined: Wed Nov 22, 2017 4:46 am

Triol TMN01-09 surface TMS Transfer issues

Post by klocium »

Only problems so far. No new purchases. Customer walked away.
Original reply
Пока только проблемы. Хотя новых закупок не было. Заказчик отказался.
darik
User avatar
Posts: 8
Joined: Thu Feb 25, 2021 8:49 am

Triol TMN01-09 surface TMS Transfer issues

Post by darik »

Avoid them. At our field shop they also sit new in the box like junk. Of Transfer downhole monitoring system (TMS), SPT-3R (Borets) and IRZ-TMS-E5-01R stuck. Also Novomet, Almaz, Elekton - but heavy and awkward to install. Etalon like Triol: readings in the shop, gone in the field from their own downhole sensor (TMS) - long cable probably.
Original reply
Обходить их стороной, у нас в цеху на месторождении они тож новые в коробке лежат как мусор. Из ТМС с протоколом трансфер у нас прижились СПТ-3R (Борец) и ИРЗ-ТМС-Э5-01Р. Есть еще новомет, алмаз, электон - но они тяжелые по весу и в установке. Эталон тож как и Триол, в цеху при проверке есть показания, в поле показания пропадают от своего же ТМСП, видимо как то влияет длинный кабель.
darik
User avatar
Posts: 8
Joined: Thu Feb 25, 2021 8:49 am

Triol TMN01-09 surface TMS Transfer issues

Post by darik »

Ildar wrote:Avoid them... Etalon like Triol: shop OK, field readings drop from own downhole sensor (TMS), long cable likely.
Though if you flash the Triol downhole monitoring system (TMS) to 48475 (was 48468), reading problems go away and it sees many Transfer downhole sensor (TMS) units.
Original reply
Обходить их стороной, у нас в цеху на месторождении они тож новые в коробке лежат как мусор. Из ТМС с протоколом трансфер у нас прижились СПТ-3R (Борец) и ИРЗ-ТМС-Э5-01Р. Есть еще новомет, алмаз, электон - но они тяжелые по весу и в установке. Эталон тож как и Триол, в цеху при проверке есть показания, в поле показания пропадают от своего же ТМСП, видимо как то влияет длинный кабель.
Хотя если прошить триоловский тмс на прошивку версии 48475 (была 48468) то проблемы с показаниями пропадают, и видит многие погружные тмс с протоколом трансфер.
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

Triol TMN01-09 surface TMS Transfer issues

Post by ALEngineer »

Triol gear is generally fine but needs drum-beating... if yours already works, do not update firmwares!
Original reply
Вообще Триол нормальное оборудование, но требует танцев с бубнами... если так случилось, что у вас всё работает ни в коем случае не обновляйте прошивки!
darik
User avatar
Posts: 8
Joined: Thu Feb 25, 2021 8:49 am

Triol TMN01-09 surface TMS Transfer issues

Post by darik »

Fine maybe for KSU menu readability, but new Triol VSDs arrived and trouble started - Ud max trips, input-voltage calibrations drift so far menu cal cannot reach nominal (swap NX or BV6 board), and with PMM pumps constant MTZ/ZP stops even with Triol-recommended setpoints.
Original reply
Нормальное разве что по читабельности меню КСУ, но пришли станции управления Триол новые, и пошло поехало, то по Udmax встают, то калибровки вх напряжения уходят на столько, что через меню калибровки до номинального не откалибруешь, приходится менять плату NX либо БВ6, с вентильными насосами вообще постоянно идут остановки по МТЗ и ЗП, и даже с уставками рекомендуемыми от Триола.