Triol PMM AK-06 short on Ud or switching unit

Post by Vdj »

Triol PMM AK-06 VSD. On start it reports a short on Ud or the switching unit. What could that be?
IMG_20191213_173441.jpg
Original topic
Станция Триол ВД АК-06 Запускаю станцию, пишет авария КЗ в Ud либо блок включения, с чем это может связано быть?
You do not have the required permissions to view the files attached to this post.
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Re: Triol PMM AK-06 short on Ud or switching unit

Post by baralgin1983 »

We had this situation the other day. We have a total of IGBT-2 modules for phase V. Replaced and VSD is already in operation.
Original reply
Данная ситуация была у нас на днях. У нас итог, модуля IGBT-2шт по фазе V. Заменили и СУ у же в работе.
mr.vladimir2011@inbox.ru
User avatar
Posts: 1
Joined: Wed Jun 24, 2020 11:06 pm

Re: Triol PMM AK-06 short on Ud or switching unit

Post by mr.vladimir2011@inbox.ru »

Evgeniy, how did you find out that IGBT-2 is specifically for phase V
Original reply
Евгений, как выяснили что IGBT-2 именно по фазе V
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Re: Triol PMM AK-06 short on Ud or switching unit

Post by baralgin1983 »

Using the dialing method through a light bulb. Hearth power supply 1.5V for control
Original reply
Методом прозвонки через лампочку. Подовая питание 1.5в на управление
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Re: Triol PMM AK-06 short on Ud or switching unit

Post by baralgin1983 »

Using the dialing method through a light bulb. Hearth power supply 1.5V for control. There is a diagram on the module. When you connect a light bulb, it turns on at half incandescence. When 1.5V power is supplied to the control, it operates at full power.
When applying 1.5V power to the control, change the polarity, this checks the opening or closing of the period. You should only use a 220V incandescent light bulb.
Original reply
Методом прозвонки через лампочку. Подовая питание 1.5в на управление. На модуле есть схема. При подключение лампочки она будит гореть в половину накаливания. Пр подаче питания 1.5в на управление она за гордиться в полную мощность.
При подаче питания 1.5в на управление меняй полярность, этим проверяем открытие или закрытие периода. Использовать надо только лампочку накаливания 220в.