Temperature sensors in VSD ASUDN -1 Elekton

Elekton ESP VFDs / VSDs. Topics migrated from the nasosforum.ru archive.
Rama8992
User avatar
Posts: 10
Joined: Wed Oct 10, 2018 12:41 am

Temperature sensors in VSD ASUDN -1 Elekton

Post by Rama8992 »

Hello Etsnschiki Who can tell me where the temperature sensor is located that displays the temperature on the controller (to be more precise, the temperature of the controller) it says 254 degrees for me and does not turn on the heating of the controller, but the screen floats the temperature is low
As I understand it, he caught the glucan or something was wrong with the contact
Has anyone encountered the problem?
Original topic
Здравствуйте Эцнщики Кто подскажет где находится датчик температуры который выводит температуру на контроллер (если быть точнее температура контроллера) он у меня кажет 254 градуса и не включает подогрев коннтроллера же экран плывет температура низкая
я так понял он поймал глюкана либо с контактом что то не то
Может кто сталкивался с проблемой
Rama8992
User avatar
Posts: 10
Joined: Wed Oct 10, 2018 12:41 am

Temperature sensors in VSD ASUDN -1 Elekton

Post by Rama8992 »

Guys, tell me where the temperature sensor of the controller is located Station ASUDN-1 Elekton
The sensor has glitched and shows +245 degrees, which is why the heating of the controller does not turn on, maybe it’s a contact problem, what can I do?
Original reply
Ребят подскажите где находится датчик температуры контроллера Станция АСУДН-1 электон
Датчик глюканул показывает +245 градусов из за этого не включается подогрев контроллера может дело в контакте что можно предпринять ?
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Temperature sensors in VSD ASUDN -1 Elekton

Post by ALEngineer »

Please don't create more topics! The topic was temporarily removed from the VSD Elekton section, because... manufacturer was not specified. If you don't see your topic in the same place, check its availability in the "Latest Discussions" section.
Original reply
Не плодите пожалуйста темы! Тема временно была вынесена из раздела СУ Электон, т.к. не был указан производитель. Если не видите вашу тему на прежнем месте, посмотрите ее наличие в разделе "Последние обсуждения".
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Temperature sensors in VSD ASUDN -1 Elekton

Post by ALEngineer »

On the topic: display temperature sensors (like the backlight) are usually attached directly to the display (oil), or filled with compound, or simply stuck with some kind of electrical tape. Usually (as I imagine) this is a thermistor (thermistor).

P.S. I didn’t immediately see that we were talking about the controller sensor, I think the principle is the same... but of course it’s not stuck to the glass :)

Yandex to help you: https://yandex.ru/images/search?text=thermistor
Original reply
По теме: датчики температуры дисплеев обычно (как и подсветка) крепятся непосредственно к дисплею (масло масляное), либо залиты компаундом, либо просто приляпаны какой нибудь изолентой. Обычно (я так представляю) это терморезистор (термистор).

P.S. сразу не увидел, что речь про датчик контроллера, думаю принцип тот же... но только естественно не к стеклу приляпан :)

Яндекс Вам в помощь: https://yandex.ru/images/search?text=терморезистор
chernyi-abdulla
User avatar
Posts: 8
Joined: Tue Oct 23, 2018 1:51 pm

Temperature sensors in VSD ASUDN -1 Elekton

Post by chernyi-abdulla »

As far as I know, ASUDN Elekton is some kind of modified frequency generator, which means VFD there is either Elekton-9.1 or Elekton-10. There are no thermistors in these controllers, there are integrated temperature sensors on the board with the display and buttons, in Elekton-9 it’s like DS1620, and in Elekton-10 I don’t know, it’s some kind of three-legged crap. Accordingly, if you see some curved readings, then the problem may be in the exchange of the thermometer with the main processor (non-contact in the cable between the boards), or a glitch in the controller software. As an option for El-09 - try to take a display board from a “known healthy” controller, or just put the inter-board cable in and out several times, then VFD in the cold, since street conditions now allow it. In el-10 there is still a percentage on the display board, so if everything is displayed on the display, then the exchange with the “main” is normal, but you can narrow down the circle of infected people by replacing the boards.
Original reply
Насколько знаю, то АСУДН Электон - это какой-то модифицированный частотник, значит КСУ там или Электон-9.1 или Электон-10. В этих контроллерах нет терморезисторов, на плате с дисплеем и кнопками стоят интегральные датчики температуры, в Электоне-9 вроде DS1620, а в Электоне-10 не знаю, какая-то трехногая хрень. Соответственно, если вы видите какие-то кривые показания, то проблема возможно в обмене градусника с основным процом (неконтакт в шлейфе между платами), либо глюк в софте контроллера. Как вариант для Эл-09 - попробуйте взять дисплейную плату от "заведомо здорового" контроллера, либо просто межплатный шлейф сунул-вынул несколько раз, потом КСУ на мороз, благо уличные условия сейчас позволяют. В эл-10 на дисплейной плате ещё проц, поэтому если на дисплей всё выводится, то обмен с "главным" в норме, но сузить круг инфицированных путем подмена плат можно.
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Temperature sensors in VSD ASUDN -1 Elekton

Post by ALEngineer »

I agree with what was said above, except for one thing, namely the type of sensor, it is of course more logical to use a digital channel, but the starter topic writes that the readings are +254 degrees, respectively, with a short circuit. or a break, the digital sensor would simply not produce any information (there would be dashes instead of readings), and the analog one would transmit either a zero level or infinity, BUT the readings would be transmitted, which is what we see.
Original reply
Соглашусь с выше сказанным, кроме одного, а именно типа датчика, логичнее конечно использовать цифровой канал, но топик стартер пишет, что показания +254 градуса, соответственно, при к.з. или обрыве цифровой датчик не выдал бы просто ни какой информации (имелись бы прочерки вместо показаний), а аналоговый будет передавать либо нулевой уровень, либо бесконечность, НО показания будут передаваться, что мы и видим.
udar17
User avatar
Posts: 10
Joined: Thu Jan 31, 2019 1:50 am

Temperature sensors in VSD ASUDN -1 Elekton

Post by udar17 »

The orderly writes everything correctly. The temperature in the Elekton-09 controller will be measured by DS1620. The number 254 may be displayed when there is no connection with it. The interface of this microcircuit is curved, so there may be such a number. It is installed above the cable. The indicator is not frozen. The indicator adjusts the contrast depending on the temperature. Now at a temperature of 254°C the contrast is at a minimum. Forcing the heating on will not solve the problem.
Original reply
Всё правильно Санитар пишет. Температуру в контроллере Электон-09 измерят DS1620. Число 254 может отображаться при отсутствии связи с ней. Интерфейс у этой микросхемы кривой так что может быть такое число. Установлена она над шлейфом. Индикатор не замёрз. У индикатора регулируется контраст в зависимости от температуры. Сейчас при температуре 254°С контраст на минимуме. Принудительным включением подогрева проблему не решить.