SUT tap voltage vs VSD supply

Discuss step-up and step-down transformers, surface cables, and power infrastructure for ESP systems. Share expertise on electrical setups and safety
DmitriiV
Posts: 4
Joined: Sat Jun 04, 2016 4:23 am

SUT tap voltage vs VSD supply

Post by DmitriiV »

Hello.

Tap voltage, by plain transformer theory, should track supply voltage. Some colleagues say it is set as a fixed value instead. Which is correct?
Original topic
Здравствуйте!

Напряжение отпайки, судя по принципу работы трансформатора, должно зависеть от входного напряжения сети. Некоторые коллеги утверждают, что это не так и оно выставляется постоянным значением. Какой из вариантов верный?
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

SUT tap voltage vs VSD supply

Post by ALEngineer »

A transformer does not stabilize voltage - that is a different device.

Output tracks input: change the input by a ratio, and the output moves by the same ratio. Nameplate voltages are reference values for nominal supply (380 V, 220 V, etc.).

To get the real output at today's bus voltage, compute the turns ratio. Example: nameplate primary 380 V, tap (secondary) 2100 V → ratio ≈ 2100/380 ≈ 5.53. At 300 V in you get about 300×5.53 = 1659 V out; at 200 V in → about 1106 V out, and so on.
Original reply
Трансформатор не имеет функции стабилизации напряжения, это совсем другое устройство.
Напряжение на выходе зависит от напряжения на входе, во сколько раз изменился вход, во столько же раз изменится и выход. Напряжения на бирке трансформатора указывается справочно, для номинального напряжения (380, 220 и т.п.).
Рассчитать какое напряжение будет выдавать трансформатор при текущем входном напряжении, можно вычислив коэффициент трансформации.
Например: Трансформатор рассчитан на номинальное входное напряжение 380 В, отпайка (выходное напряжение) равно 2100 В (все эти данные можно найти на табличке трансформатора) коэффициент трансформации можно вычислить разделив вторичное напряжение на первичное 2100/380 получаем приблизительно 5,53. Теперь легко вычислить выходное напряжение при любом входном, например при 300 В на выходе будет 300*5,53=1659 В, при входном напряжении 200 В, на выходе будет 200*5,53=1106 и т.п.
DmitriiV
Posts: 4
Joined: Sat Jun 04, 2016 4:23 am

SUT tap voltage vs VSD supply

Post by DmitriiV »

Thanks, got it.

Are there ESP setups with voltage stabilizers? Also: I know there is an input-voltage setpoint on the VSD - what value is typical?
Original reply
Спасибо, понял.
А существуют схемы УЭЦН со стабилизаторами напряжения? И ещё момент: на сколько я знаю существует уставка по входном напряжению. Чему как правило она равна?
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

SUT tap voltage vs VSD supply

Post by ALEngineer »

Why bother with a stabilizer? VFDs are common now - within reason they put out whatever voltage and frequency you need.

Per the electrical code, if I recall, voltage tolerance is about ±12%. In the field, VFDs usually cope from about -20% to +15% on the supply. A lot still depends on run frequency, tap, equipment size, how the ramp curve is set, protections, and so on - that is a long separate topic.

These VSDs are fairly forgiving on voltage scatter; they hate supply-frequency drift. About 1% is already critical - the grid should stay a clean 50 Hz. Maybe that is better now, but five years ago diesel gensets caused a lot of grief.
Original reply
А смысл в стабилизаторе? Сейчас широко применяют СУ с частотным регулированием, они в разумных пределах выдают на выходе любое напряжение и частоту.
По ПУЭ если не ошибаюсь допуск на напряжение плюс минус 12%, на практике СУ с ЧР нормально работают при уходе питающего напряжения от минус 20% до плюс 15%. Опять же многое зависит от рабочей частоты, напряжения отпайки, мощности оборудования, на какую частоту выставлена кривая разгона, как выставлены защиты и т.п. это отдельная большая тема и надо знать и понимать как работают СУ с ЧР. Данные станции не очень боятся разброса по напряжению, они боятся ухода частоты питающей сети, 1% это критично, сеть должна выдавать идеальные 50Гц. (может сейчас это уже и не так, но лет 5 назад много проблем было при питании от дизельных подстанций).