SUT tap tables do not match nameplate vs cover

Discuss step-up and step-down transformers, surface cables, and power infrastructure for ESP systems. Share expertise on electrical setups and safety
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

SUT tap tables do not match nameplate vs cover

Post by ALEngineer »

SUT nameplate vs cover tap tables. I have seen cases where the tags do not match the tables on the SUT tank and on the cover over the secondary leads. In practice, trust the tag on the transformer tank - covers get mixed up on assembly. Sometimes the cover plate also swaps the P1 and P2 labels, so double-check carefully. A wrong tap usually shows up as high running currents.
Original topic
Сталкивался с проблемой не соответствия бирок с таблицами на корпусе ТМПН и на крышке закрывающей выводные концы. По опыту следует сверяться с биркой находящейся на корпусе трансформатора, т.к. по всей видимости случаются ошибки при монтаже крышек.
Так же бывает, что в табличке на крышке поменяны местами надписи П1 и П2, тоже сверяться следует внимательнее. О том что не правильно выставлена отпайка, свидетельствуют завышенные рабочие токи.