Good day, guys - can you tell me how to correctly calculate VSD power?
Original topic
Добрый день, ребят подскажите как правильно расчитать мощность СУ ?
ALEngineer
Site Admin
User avatar
Posts: 249
Joined: Wed Mar 18, 2026 2:51 pm

Sizing a VSD by motor power

Post by ALEngineer »

Divide the actual step-up transformer tap voltage by 380, multiply the result by the motor rated current. That gives the minimum required VSD current. For VSD, choose with about a 30% margin; 5-10% is enough for direct start. For heavy starts or stuck-pump (free-up) conditions, increase the margin accordingly based on actual stuck-pump currents - same calculation. For VSD, to be safe: divide by 360 instead of 380.
The same calculated current is used to select cable size for surface equipment wiring.
Original reply
Фактическую отпайку делить на 380, на полученную цифру умножить номинальный ток двигателя. Получим минимально необходимый ток станции управления. СУ ЧР выбирать с запасом процентов 30, прямой пуск 5-10 процентов достаточно. Если тяжелые запуски или расклинивание, соответственно запас больше, исходя из фактических токов при расклинивании, расчет аналогичен. Для СУ ЧР, что бы наверняка: разделить не на 380, а на 360.
Исходя из этого же расчетного тока подбирают сечение кабеля для обвязки НО.
asman4ik666@mail.ru
Posts: 2
Joined: Mon Apr 11, 2016 2:09 am

Sizing a VSD by motor power

Post by asman4ik666@mail.ru »

VSD CALCULATION:

tap voltage times rated current divided by 380, times 1.2
Original reply
РАСЧЕТ СУ:

отпайку умножить на ток номинальный делить на 380 и умножить на 1.2