Short circuit fault in Ud or switching unit Triol PM AK-06

Triol ESP VSDs. Topics migrated from the nasosforum.ru archive.
Vdj
User avatar
Posts: 4
Joined: Fri Dec 13, 2019 7:23 am

Short circuit fault in Ud or switching unit Triol PM AK-06

Post by Vdj »

Station Triol PM AK-06 I start the station, it says short circuit fault in Ud or the switching unit, what could this be connected with?
IMG_20191213_173441.jpg
Original topic
Станция Триол ВД АК-06 Запускаю станцию, пишет авария КЗ в Ud либо блок включения, с чем это может связано быть?
You do not have the required permissions to view the files attached to this post.
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Short circuit fault in Ud or switching unit Triol PM AK-06

Post by baralgin1983 »

We had this situation the other day. We have a total of IGBT-2 modules for phase V. Replaced and VSD is already in operation.
Original reply
Данная ситуация была у нас на днях. У нас итог, модуля IGBT-2шт по фазе V. Заменили и СУ у же в работе.
mr.vladimir2011@inbox.ru
User avatar
Posts: 1
Joined: Wed Jun 24, 2020 11:06 pm

Short circuit fault in Ud or switching unit Triol PM AK-06

Post by mr.vladimir2011@inbox.ru »

Evgeniy, how did you find out that IGBT-2 is specifically for phase V
Original reply
Евгений, как выяснили что IGBT-2 именно по фазе V
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Short circuit fault in Ud or switching unit Triol PM AK-06

Post by baralgin1983 »

Using the dialing method through a light bulb. Hearth power supply 1.5V for control
Original reply
Методом прозвонки через лампочку. Подовая питание 1.5в на управление
baralgin1983
User avatar
Posts: 3
Joined: Wed Jan 08, 2020 1:13 am

Short circuit fault in Ud or switching unit Triol PM AK-06

Post by baralgin1983 »

Using the dialing method through a light bulb. Hearth power supply 1.5V for control. There is a diagram on the module. When you connect a light bulb, it turns on at half incandescence. When 1.5V power is supplied to the control, it operates at full power.
When applying 1.5V power to the control, change the polarity, this checks the opening or closing of the period. You should only use a 220V incandescent light bulb.
Original reply
Методом прозвонки через лампочку. Подовая питание 1.5в на управление. На модуле есть схема. При подключение лампочки она будит гореть в половину накаливания. Пр подаче питания 1.5в на управление она за гордиться в полную мощность.
При подаче питания 1.5в на управление меняй полярность, этим проверяем открытие или закрытие периода. Использовать надо только лампочку накаливания 220в.