RS-485

Post by DmitryEcnKiller »

Good day. The situation is the following: when connecting the Borets ESP VSD to the bus, it sags the peak amplitude of the digital signal pulses from the other stations. RS-485 line. What could this be related to? What are the possible solutions?
Original topic
Добрый день. Ситуация следующая: су эцн борец при подключении к шлейфу просаживает амплитудное амплитудное значение импульсов цифрового сигнала остальных станций. Линия RS-485. С чем это может быть связано? Какие пути решения?
User avatar
kolt86
Posts: 0
Joined: Mon Feb 04, 2019 3:11 am

RS-485

Post by kolt86 »

120 kOhm resistors on RS-485 are not uncommon on Borets units, but they don't significantly affect the sag. Most likely the pull-up circuits have failed and the port starts being powered from the line, sagging the voltage. There is also a galvanic isolation board - need to check its resistance.
Original reply
Не редко попадаются борцы с резистором 120 kOm на rs-485, но он не сильно влияет на просадку. Скорее всего цепи подтяжки вышли из строя и порт начинает питаться от линии просаживая напругу. Там ещё плата гальванической развязки есть, нужно проверить её сопротивление.