- Run TMCN_Control_v.2.302 Pro.exe
- Open the "setpoints" tab and click the circular-arrow button (left column) to read setpoints.
Change 0x111 "sync-pulse amplitude detection threshold" - default 30; you can lower to 25 or 20.
- Find the row "sync-pulse amplitude detection threshold" (often row 18):
- Enter 25 or 20 in the right column and tick the checkbox.
If within a couple of minutes with the ESP motor stopped there are still no readings, change 0x110 "half amplitude window range" - default 12; you can raise to 14 or 16.
- That setpoint is usually row 17:
- Enter 14 or 16 in the right column and tick the checkbox.
Done. Download the program here (attachment).
Instruction as a separate file (attachment). Not my authorship: Testing VSD RS-485 output to SCADA
Scan / image text translation (original scan kept as attachment below):
2.4.3 When using port "1 RS-232" to connect a PC to the SIU (TMS), use interconnect cable No. 1 TsTKD 083.01-02 made by Elekton. Figure 1 shows the pinout of cable No. 1 for the PC connection.
Figure 1 - Pinout of cable No. 1 (both ends DB9F, X1 and X2):
Code: Select all
Straight-through
X1 pin 2 -- X2 pin 2
X1 pin 3 -- X2 pin 3
X1 pin 5 -- X2 pin 5
Jumpers on each connector
pins 1, 4, 6 together (DCD / DTR / DSR)
pins 7 and 8 together (RTS / CTS)
pin 9 not connected
From the Elekton TMS-3 OM page (TsTKD 228 OM) in the screenshot:
Check SIU output data and data to the controller or other devices. In the SIU, check and adjust analog output voltage ranges (10 V, 4 V) to match the VSD analog inputs. Check and correct other downhole monitoring system (TMS) setpoints. Read the internal history. Correct the internal clock (with Elekton-series VSDs the SIU clock syncs to the controller automatically).
ATTENTION: TMSN-3 SIUs are interchangeable. They work with TMSP-3 and TMSP-2 downhole sensors (TMS). They are not designed to work with TMSP-1.
2.4.4 Pump-unit protection from downhole parameters: data update is typically 40 to 55 s. Factory setting for continuous insulation-resistance (Riso) measurement time is 20 s. Set protection trip delays and AR delays to not less than 1 minute.
2.4.5 The downhole monitoring system (TMS) is powered off together with the VSD automation.
Screenshot of TMC (v. 2.3.0.2) Setpoints tab (TMS-3 address 1, COM1 9600). The two registers used in this procedure:
Code: Select all
+--------+--------------------------------------+---------+----------+
| Addr | Name | Default | Try |
+--------+--------------------------------------+---------+----------+
| 0x111 | sync-pulse amplitude detection | 30 | 25 or 20 |
| | threshold (often row 18) | | |
+--------+--------------------------------------+---------+----------+
| 0x110 | half amplitude window range | 12 | 14 or 16 |
| | (usually row 17) | | |
+--------+--------------------------------------+---------+----------+
Original topic
• Подключить ноутбук к ТМСН-3
• запустить программу TMCN_Control_v.2.302 Pro.exe
• выбрать вкладку «уставки», и щелкнуть кнопку с круговой стрелкой (левый столбец) для считывания уставок.
изменить 0x111 "порог обнаружения амплитуды синхроимпульса" - задано 30, можно уменьшить - 25, 20.
• ищем строчку с уставкой «порог обнаружения амплитуды синхроимпульса (это может быть строчка №18):
• на правом столбце вводим 25 или 20, и рядом ставим галочку;
• если в течение Если в течении пары минут при остановленном ПЭД показаний нет, то необходимо изменить:
0x110 "половина диапазона амплитудного окна" - задано 12, можно увеличить - 14, 16.
• эта уставка обычно на строчке №17:
• на правом столбце вводим 14 или 16, и рядом ставим галочку..
Всё
Скачать программу можно тут:
Инструкция скачать отдельным файлом:
Авторство не мое: Testing VSD RS-485 output to SCADA (Region-2000, Telescop, etc.)
• запустить программу TMCN_Control_v.2.302 Pro.exe
• выбрать вкладку «уставки», и щелкнуть кнопку с круговой стрелкой (левый столбец) для считывания уставок.
изменить 0x111 "порог обнаружения амплитуды синхроимпульса" - задано 30, можно уменьшить - 25, 20.
• ищем строчку с уставкой «порог обнаружения амплитуды синхроимпульса (это может быть строчка №18):
• на правом столбце вводим 25 или 20, и рядом ставим галочку;
• если в течение Если в течении пары минут при остановленном ПЭД показаний нет, то необходимо изменить:
0x110 "половина диапазона амплитудного окна" - задано 12, можно увеличить - 14, 16.
• эта уставка обычно на строчке №17:
• на правом столбце вводим 14 или 16, и рядом ставим галочку..
Всё
Скачать программу можно тут:
Инструкция скачать отдельным файлом:
Авторство не мое: Testing VSD RS-485 output to SCADA (Region-2000, Telescop, etc.)