For
VSD supply we use a
4-core cable, because the station needs a solidly grounded-neutral source - one conductor does both PN and PE. Inside the
VSD that neutral (also earth) lands on the enclosure. The jumper between
VSD and
SUT is a
3-core cable: the
SUT neutral is isolated and on many models is simply missing on the LV side. The
SUT HV-side neutral goes to the downhole monitoring system (TMS) or to the
IMD board. That wire needs tougher insulation than the supply cables - high voltage can appear on it in a fault. Earthing: every item (
VSD,
SUT, filter, etc.) gets its own earth loop (triangle or 5 rods in a row), and those earths are bonded together with a dedicated conductor or a metal rack that is also earthed. Everything bonded; each item its own loop. Where to look: equipment O&M manuals and standards such as
Rosneft ETT.
Original reply
Для подключения питания СУ используется 4х жильный кабель, т.к. для питания СУ требуется источник с глухо-заземленной нейтралью, т.е. один проводник выполняет функцию PN и PE. В СУ данная нейтраль (она же земля) подключается к корпусу.
В качестве перемычки между СУ и ТМПН используется 3х жильный кабель, т.к. нейтраль ТМПН заизолирована и во многих моделях трансформаторов просто отсутствует по низкой стороне.
Нейтраль ТМПН по высокой стороне, подключается к системе телеметрии, либо к плате ПКИ (УКИ). К изоляции этого провода требования выше чем к питающим кабелям, т.к. возможно появление высокого напряжения в случае не штатной работы оборудования.
Особые требования к заземлению, каждый элемент (СУ, ТМПН, Фильтр и т.п.) заземляются отдельным контуром (либо треугольник, либо 5 штырей в ряд) и заземление всех элементов связываются между собой, либо отдельным проводником, либо металлической эстакадой (тоже отдельно заземленной). В общем все должно быть заземлено и на каждый элемент свой контур.
По поводу того где искать, все описано в руководствах по эксплуатации на оборудование и стандартах, например таких как ЕТТ для Роснефти.