Etalon VSD motor-load display

Post by novomet19871 »

Hi all. Which board on an Etalon VSD do you swap when motor load stops showing up? Every other parameter is there except load.
Original topic
Доброго времени суток всем!!!! Подскажите какую плату нужно менять когда станция управления перестала показывать загрузку двигателя? Всё пораметры есть кроме загрузки!!!
chitos3572
Posts: 12
Joined: Wed Sep 10, 2014 11:59 pm

Re: Etalon VSD motor-load display

Post by chitos3572 »

Good afternoon No board affects the loading readings. This is the calculated value. It may be affected by incorrect connection of wires from the output current measurement transformers, due to the incorrect phase of the current relative to the output voltage.
Original reply
Добрый день! Никакая плата на показания загрузки не влияет. Это расчетное значение. Может влиять неправильное подключение проводов от трансформаторов измерения выходного тока, из-за неправильной фазы тока относительно выходного напряжения..