ESP current setpoints on Etalon-03 VFD

Post by Jawa350638 »

Good night colleagues - how are ESP current setpoints adjusted on the Etalon-03 VFD?
Original topic
Доброй ночи коллеги, вопрос следующего характера, как корректируются токи в Эталон -03 ЧР ?
chitos3572
Posts: 12
Joined: Wed Sep 10, 2014 11:59 pm

Re: ESP current setpoints on Etalon-03 VFD

Post by chitos3572 »

Good afternoon
In VSD Etalon the currents are adjusted in the menu item "5 Correction factor", parameters 5.02, 5.04, 5.06. Or go to menu item 1/1.1 Measured parameters/Basic, select the current of the phase of interest (items 02, 03, 04), press “Enter” and enter the desired parameter value. (this correction mode may not be available in all versions of operator panel software)
Original reply
Добрый день!
В СУ Эталон токи корректируются в пункте меню "5 Коэфф.коррекции", параметры 5.02, 5.04, 5.06. Или заходим в пункт меню 1/1.1 Измеряемые параметры/Основные, выбираем ток интересующей фазы (пункты 02, 03, 04), нажимаем "Ввод" и вводим желаемое значение параметра. (данный режим коррекции может быть доступен не во всех версиях ПО панели оператора)