Elekton VSD stops on surface TMS link loss

Post by Rama8992 »

Guys - Elekton VSD stops on loss of link with the Elekton SIU (surface interface unit, TMS). We checked downhole with a simulator and a multimeter, then the SIU (surface interface unit, TMS) unloaded - all OK. If I am right, surface talks to the station over RS-485 - maybe that is the issue? Hookup checked OK. We have not pulled SIU (surface interface unit, TMS) data yet - there is a U_interference column; could that be the cause?
Original topic
Ребят такая проблема СУ электон останавливается по причине потери связи с наземным блоком тоже электон значит приехали проверили сам погружной и имитатором и так мультиком потом на холостую проверили сам тмсн тоже все в порядке . Если правильно понимаю сам наземный со станцией общается по rs 485 может здесь какая проблема кто сталкивался подключение все верно проверили . Ещё правда не снимали данные самого наземного блока там есть колонка u помехи может ли быть в ней причина ??
ALEngineer
Site Admin
User avatar
Posts: 354
Joined: Wed Mar 18, 2026 2:51 pm

Elekton VSD stops on surface TMS link loss

Post by ALEngineer »

Backing the thread - Elekton blocks love this behavior. 7-8 years ago IRZ did the same; almost always the pad ground loop or ungrounded gear. We scoped noise on the HV lead with a 100x probe.

Another cause: long downhole cable (3000 m+) - signal attenuates. Lately I also see Elekton issues at relatively shallow ~2000 m.
Original reply
Поддерживаю тему, любят так себя вести блоки Электона, раньше (лет 7-8 назад) ИРЗ себя так вел, с ними почти всегда находилась проблема в заземляющем контуре самой площадки, либо оборудование не было заземлено. Осциллографом измеряли уровень помех на ВВ проводе, при помощи щупа делителя на 100.
Еще причина может крыться в большой длине погружного кабеля (3000м и более), сигнал затухает. Но в последнее время с Электоном сталкиваюсь с проблемой и на относительно небольших глубинах, около 2000м.
udar17
User avatar
Posts: 13
Joined: Thu Jan 31, 2019 1:50 am

Elekton VSD stops on surface TMS link loss

Post by udar17 »

Ramazan wrote:Guys - Elekton VSD stops on loss of link with the Elekton SIU (surface interface unit, TMS)... U_interference column - could that be the cause?
First find where the link drops. The log records loss with downhole sensor (TMS) or SIU (surface interface unit, TMS). If the downhole monitoring system (TMS) is new it runs Transfer - pull event logs and call service.
Original reply
Ребят такая проблема СУ электон останавливается по причине потери связи с наземным блоком тоже электон значит приехали проверили сам погружной и имитатором и так мультиком потом на холостую проверили сам тмсн тоже все в порядке . Если правильно понимаю сам наземный со станцией общается по rs 485 может здесь какая проблема кто сталкивался подключение все верно проверили . Ещё правда не снимали данные самого наземного блока там есть колонка u помехи может ли быть в ней причина ??
Сначала определите где пропадает связь. В журнале фиксируется потеря связи с ТМСП или ТМСН. Если ТМС свежий, то он работает под транфером и лучше сразу снять журналы событий и обратиться к сервисникам.
Rama8992
User avatar
Posts: 13
Joined: Wed Oct 10, 2018 12:41 am

Elekton VSD stops on surface TMS link loss

Post by Rama8992 »

Link loss is specifically with SIU (surface interface unit, TMS), not the downhole unit.
Original reply
Потеря связи именно с ТМСН с наземным а не с погружником
udar17
User avatar
Posts: 13
Joined: Thu Jan 31, 2019 1:50 am

Elekton VSD stops on surface TMS link loss

Post by udar17 »

Hard to advise without event logs. Usually link to the SIU (surface interface unit, TMS) drops when another device on the same RS-485 port blocks the bus. Sometimes telemechanics is landed on that port and interferes with a downhole monitoring system (TMS).
Original reply
Без журналов событий конечно тяжело советовать. Обычно связь с наземном блоком ТМС пропадает когда на этот же порт RS485 подключают ещё какое-то устройство которое может блокировать шину. Иногда телемеханику подключают к этому порту и она мешает связи ТМС.
chernyi-abdulla
User avatar
Posts: 15
Joined: Tue Oct 23, 2018 1:51 pm

Elekton VSD stops on surface TMS link loss

Post by chernyi-abdulla »

As a car owner (not a shop), on car forums you state the VIN first so people can answer without "which engine, gearbox, 4WD...". Point: gear variety exploded - Elekton has ~4 controllers, Borets no fewer. "Universal" protocols bred more downhole monitoring system (TMS) flavors, each with its own bugs. That note is for this asker and for how questions are asked on the whole forum.

To the Elekton Dev colleague: Ramazan clarified (awkwardly) that link died between SIU (surface interface unit, TMS) and controller. Why did the techs hang simulators - that checks surface-to-downhole, not surface-to-controller - instead of checking RS-485 in the VSD or swapping the SIU (surface interface unit, TMS)? They should dump all chronologies and send them to Dev if stuck. I used to hop pads too and could not always diagnose cleanly, but grabbing max info and knowing which specialist to ask is basic first-aid.

Sorry if a bit sharp - it builds up.
Original reply
Я, как автолюбитель, а не автосервисник, по всяким автовопросам обращаюсь на соответственный тематический форум по самодвижущимся экипажам, так вот там принято, прежде чем задать вопрос, указать vin, дабы компетентные люди по комплектации сразу могли дать ответ без запросов "а какой двиг, коробка, 4wd или fwd и тп". Эт всё к чему, оборудования у всех развелось черте сколько, у того же Электона контроллеров штуки 4, у Борца не меньше. С появлением "универсальных" протоколов разновидностей ТМС понаплодилось. И у всего этого многообразия свои болячки. Эти замечания не только к данному просителю, а вообще к организации вопросов на всем форуме.
К товарищу Разрабу из Электона: Рамазан уточнил (хоть и коряво), что пропала связь между наземным блоком и контроллером, если так, то что у Электона за спецы, которые вместо того, чтоб проверить в СУ что как по rs485 или поменять наземку, взялись вешать имитаторы всякие, этож проверка работы наземника с погружным, а не с контроллером. Они же д.б. снять все возможные хронологии и переслать собственно Разработчику, если сами не разобрались. Я тоже скакал по кустам в своё время и не всегда мог адекватно диагностировать болезнь, но снять максимум инфы и знать какому терапевту (или проктологу) направить вопрос - это стандартный набор действий скорой помощи.
Прошу прощения за, может быть излишнюю резкость местами, но накипает.
martin_200573@mail.ru
User avatar
Posts: 2
Joined: Sat Feb 23, 2019 12:36 pm

Elekton VSD stops on surface TMS link loss

Post by martin_200573@mail.ru »

Hello - looked for a Borets VSD thread and did not find one. Answering from experience: Elekton has a quirk where downhole monitoring system (TMS) runs fine then SIU (surface interface unit, TMS)-VSD link drops. I just reboot the downhole monitoring system (TMS) - link comes back ~90%. Other 10% the downhole monitoring system (TMS) itself is bad.
Original reply
Здравствуйте ,искал тему про СУ Борец так и не нашёл .отвечаю хотя бы на ваш вопрос по своему опыту.у Электонов есть такая фишка ТМС работает всё хорошо и вдруг пропадает связь ТМСН и СУ.я делаю так просто перегружаю ТМС.И связь появляется в 90%.в другие 10% проблема в самом ТМС е.
ildus
User avatar
Posts: 40
Joined: Sun May 12, 2019 4:31 am

Elekton VSD stops on surface TMS link loss

Post by ildus »

Analyze the SIU (surface interface unit, TMS) log.
If link to downhole sensor (TMS) drops periodically, SIU (surface interface unit, TMS) setpoints can extend downhole monitoring system (TMS) run.
Original reply
журнал с ТМСН нужно анализировать.
Если периодический теряется связь с ТМСП можно уставками ТМСН продлить работу ТМС.
kolt86
User avatar
Posts: 12
Joined: Mon Feb 04, 2019 3:11 am

Elekton VSD stops on surface TMS link loss

Post by kolt86 »

On version 18.25.5 the 485 port hangs - flash the KSU with newer firmware; from 18.25.7 that issue is gone.
Original reply
С версией 18.25.5 зависает 485 порт прошивайте КСУ свежей прошивкой, с 18.25.7 такой проблемы уже нет.