If VFD contains TMS, then it measures the insulation.
1.Check if the controller is receiving data from TMS. M.b. such a situation is that, for example, the connection with TMS is not set in the settings, and VFD is trying to measure Riz with its input, but it is left in an incomprehensible state, according to the line what values \u200b\u200bwith fully operational equipment.
2. Jamb TMS, when ESP operates at zero step-up transformer and ESP there is an alternating skew voltage. When the filter is in the ground or submersible, straightening occurs, and the readings from the ground can be skewed both in + and -. But with this jamb in the foot, the insulation should be normal! Only at work ESP! During operation, you can play with the output frequency and, perhaps, the insulation readings will change, but again not predictably.
Original reply
Если в СУ стоит ТМС, то изоляцию измеряет она.
1.Проверьте, получает ли контроллер данные с ТМС. М.б. такая ситуация, что, например, в уставках не выставлена связь с ТМС, и КСУ пытается измерить Rиз своим входом, а он брошен в непонятном состоянии, соответственно черте какие значения при полностью исправном оборудовании.
2.Косяк ТМС, при работе ПЭД в нуле ТМПН и ПЭД имеется переменное напряжение перекоса. При х..вом фильтре в наземке или погружнине происходит выпрямление, и показания с наземки могут покривиться как в +, так и в -. Но при данном заложенном косяке в стопе изоляция должна быть в норме! Только в работе ЭЦН! В работе можно поиграть выходной частотой и, возможно, показания по изоляции изменятся, но опять же не предсказуемо.