Has anyone seen a Borets 06/1000 (2016) VSD show reverse phase order right at the output?

Hi all. After swapping an Elekton VSD for a Borets 06/1000 (2016), we started it near no-load.

Fifteen minutes in we checked rotation with a phase-sequence indicator and it was reverse. The kicker: wrong phase sequence at the VSD output.

Nameplate says input ABC, and the output cable was landed UVW per the marks. Controller shows forward rotation and ABC, but the VSD output is CBA.

Anyone seen this, or is it a one-off?
Original topic
Доброго времени суток коллеги, сегодня была такая ситуация: После смены СУ Электон на Борец 06/1000 2016г был произведен запуск с параметрами приближенных к Х.Х после 15 минут работы было решено проверить фазировку с помощью прибора указателя фаз, после чего было выявлено обратное вращение.

И самый главный прикол в том что на выходе со станции было не правильное чередование фаз.

По факту метки на станции идут АВС на вход с выхода UVW кабель смонтировали согласно меток фазировки.

В контролере вращение прямое чередование фаз АВС а на выходе с СУ CВА.

Кто сталкивался с таким или это единичный случай?:blink:
Serden
User avatar
Posts: 21
Joined: Wed Feb 08, 2017 4:45 am

Re: Borets 06/1000 VSD (2016)

Post by Serden »

Nothing surprising - routine case. Your Borets had been "fighting" what it thought was forward rotation before.

Don't trust a phase indicator on a VFD VSD - our practice: after every workover we spin both directions (exception: ESPs over 90 kW on direct-start VSDs). In your case it's clear: it was running in normal parameters, after the VSD swap - no-load currents, no overloads, so a broken shaft on flat ground is unlikely.

One thing left - wrong rotation direction.
Original reply
Ничего удивительного - рабочий случай, где до этого ваш Борец "боролся" для него было прямое вращение, на СУ с ЧРП веры фазоуказателю нет, у нас практика такова: после каждого ТКРСа вертим в обе стороны, (исключение ПЭДы более 90кВт на СУ прямой пуск) ,а в вашей ситуации сразу понятно, работала в рабочих параметрах, после смены СУ - токи х.х., перегрузов не было, следовательно слома вала на ровном месте тоже быть не может, остаётся одно - неверное вращение.
ALEngineer
Site Admin
User avatar
Posts: 579
Joined: Wed Mar 18, 2026 2:51 pm

Re: Borets 06/1000 VSD (2016)

Post by ALEngineer »

I don't recall exactly how Borets labels rotation direction - I think "forward" and "reverse". What likely misled you is the ABC phase sequence display in current VSD status.

That parameter means correct sequence on the INPUT (you yourself wrote input marked ABC, output UVW - and the controller matches). To change rotation, find the rotation direction setting - forward/reverse.

If the Borets has an Elektron controller, it's in the VFD settings; if it's the native Borets controller, hunt for it - I don't remember where. If rotation is correct in settings, the VSD probably came back from repair where someone swapped output leads.
Original reply
Я не помню точно как пишет Борец напрвление вращения, по моему 'прямое' и 'обратное', вас по всей видимости ввело в заблуждение отображение чередования фаз АВС в текущем состоянии СУ, этот параметр подразумевает, что на ВХОДЕ верное чередование (вы же сами пишете, что на входе маркировка АВС, а на выходе UVW, соответственно и в контроллере), что бы изменить вращение, нужно искать строки направление вращения прямое обратное, если борец с Электоновским контроллером, то в настройках чрп этот пункт, если свой родной, то ищите, не помню где он.

Если вращение верное в уставках, то скорее всего СУ пришла с ремонта, где горе электрики перепутали местами выводные кабеля.
dobrin
User avatar
Posts: 6
Joined: Thu May 18, 2017 5:21 am

Re: Borets 06/1000 VSD (2016)

Post by dobrin »

You can change output phasing in parameter 96 on Kvant-1 controller, or on Argus go to Settings / Other and select rotation direction.
Original reply
Сменить фазировку выходного напряжения в СУ можно в параметре 96,если это контроллер Квант-1 или,если это контроллер Аргус,заходим в Уставки Другие и выбираем направление вращения.
andrik-sedoy
User avatar
Posts: 53
Joined: Wed May 04, 2016 2:08 pm

Re: Borets 06/1000 VSD (2016)

Post by andrik-sedoy »

Borets are something else! Remember a batch of VSDs came to the shop - all from zero. During load test per program, after the first cycle every unit threw incoming phasing error for the whole batch! Factory engineer came and reflashed the controllers. Those were Borets 06 with Kvant controller.
Original reply
Борцы те ещё хулиганы! Помню в цэх пришла партия СУ, все с нуля, дак при обкатке на нагрузку по программе выходило, что после первого цикла работы выдавало ошибку по неправильной входящей фазировке у всей партии! В итоге приезжал инженер с завода и прошивал контроллеры. Как ра были борцы 06 с контроллером квант